Wondering if it would be okay to put 2 Ceiling Fans on one circuit if that is all that is on it? And would 14-2 be good or 12-2 with a 20 amp breaker???

Have not got that far yet or better to go with 2 15 Amp circuits one for each of the 2 fans?

Thanks,
MMeehan

DougLanglois
Re: Would it be okay to put 2 Ceiling Fans on one circuit???

Including the light, ceiling fans won't use more than 150 watts total, so 300 watts for two. Check your fans to find specific numbers.

A 15A circuit is rated for a load of 15 * 120 * 80% = 1,440W, so unless there is some bizarre and obscure code that says to the contrary I see no reason to not have two fans on one 15A circuit.

Remember though that the gauge is determined by the breaker. If you have a 20A breaker, you must use 12 gauge wire throughout. If you put 14 Ga. wire on a 20A breaker, the breaker may as well not be there since the wire will fail before the breaker trips.

JLMCDANIEL
Re: Would it be okay to put 2 Ceiling Fans on one circuit???

Sure as long as you don't exceed the capacity of the circuit you can have as many as you want.

Jack

DougLanglois
Re: Would it be okay to put 2 Ceiling Fans on one circuit???

If you're putting in a new circuit, by the way, just go with a 20A breaker and 12ga. The cost difference is negligible, and while 12ga. is a little harder to work with it's not that big a deal.

That way you have much more capacity for future upgrades if needed.

JLMCDANIEL
Re: Would it be okay to put 2 Ceiling Fans on one circuit???
DougLanglois wrote:

Remember though that the gauge is determined by the breaker. If you have a 20A breaker, you must use 12 gauge wire throughout. If you put 14 Ga. wire on a 20A breaker, the breaker may as well not be there since the wire will fail before the breaker trips.

A little over dramatization there Doug, Although using 14 ga wire on a 20 amp breaker is not code it is also not likely to cause a failure of the wire.
Jack

MMeehan
Re: Would it be okay to put 2 Ceiling Fans on one circuit???

Thanks but will be controlling each fan with 2 3-Way switches so it might get a bit more in cost with 12-3 between the 2 3-Way switches. being 2 of the 3-Ways will be on the 1st Flr and the others on the 2nd where the fans will be. But it is a loft layout. So the 2 3-Ways will be for convenience of not having to run upstairs to turn them off.

Also yes 14 gauge wiring for 15 Amp and 12 gauge wiring for 20 Amp.

Appreciate the info.

MMeehan

DougLanglois
Re: Would it be okay to put 2 Ceiling Fans on one circuit???
JLMCDANIEL wrote:

A little over dramatization there Doug, Although using 14 ga wire on a 20 amp breaker is not code it is also not likely to cause a failure of the wire.
Jack

It won't cause a failure of the wire, no. But it does make the wire the weakest part in the circuit, which is contrary to the goals of the circuit breaker - to protect the wire. That's my understanding of the reason for the code.

DougLanglois
Re: Would it be okay to put 2 Ceiling Fans on one circuit???

Sorry, didn't mean that to sound snippy. Long day at work and I'm feeling punchy. Time for a beer.

JLMCDANIEL
Re: Would it be okay to put 2 Ceiling Fans on one circuit???

Code requirements are for worst case scenarios and takes into account voltage drop and heat production. The code has a large safety margin built in. In panel wiring 14 ga wire is used for up to 42 amps. It is however always good to point to and comply with code requirements.
Jack

DougLanglois
Re: Would it be okay to put 2 Ceiling Fans on one circuit???
JLMCDANIEL wrote:

Code requirements are for worst case scenarios and takes into account voltage drop and heat production. The code has a large safety margin built in. In panel wiring 14 ga wire is used for up to 42 amps. It is however always good to point to and comply with code requirements.
Jack

I did not know that. Learn something new every day.

And this is why I should probably stick to asking questions, instead of answering them :D

MMeehan
Re: Would it be okay to put 2 Ceiling Fans on one circuit???

If 12 gauge was as low cost it was when it was White and not Yellow I would go with the 12 gauge but these days it gets a bit pricey I have already used 750 ft of 14-2 and 150 ft of 12-2 and I still need to run the 2 Ceiling Fans circuit and the switches runs. And now I have to run another 12 gauge for the bath room Heater, Fan & Light. Though I am not funding the materials it is starting to get up there and no fixtures yet... But I guess that is the Cost for having your own Hunting Cabin though not mine...

Though I do have some White 12 Romex here at my house from years past, today they like to see the yellow to know it is 12 gauge...

Thanks Guys for the all the help and input.