steam heat,single pipe system

i've been losing water out of my boiler.i have no leaks and i've changed my vents on the radators and still filling or adding water.more than i ever have boilers only 10 years old.any suggestions

johnjh2o
Re: steam heat,single pipe system

The two main reasons for loosing water from a one pipe steam system are a leak in the system or a steam vent that is leaking steam. It could also be that the relief valve is opening. This could be caused by a malfunctioning relief valve or to high of a steam pressure.

John

franktrak
Re: steam heat,single pipe system

thanks john,i think its my heat exchanger. you can hear the steam going up the smoke pipe. thanks again

johnjh2o
Re: steam heat,single pipe system
franktrak wrote:

thanks john,i think its my heat exchanger. you can hear the steam going up the smoke pipe. thanks again

Sorry to hear that Frank. Looks like it's time for a new boiler.

John