apbj68
Rheem Furnace Problem

I have a Rheem furnace model# rrka-a024jk08e. In the past week I have had to replace the main control board because it was burnt up. After replacing, there is no power going to the direct spark igniter. The blower fan and inducer fan run though, even with the thermostat in the off position.I bypassed the limit switch and the gas pressure switch. Still did not work. Any help would be appreciated..

BigWalt
Re: Rheem Furnace Problem
apbj68 wrote:

I have a Rheem furnace model# rrka-a024jk08e. In the past week I have had to replace the main control board because it was burnt up. After replacing, there is no power going to the direct spark igniter. The blower fan and inducer fan run though, even with the thermostat in the off position.I bypassed the limit switch and the gas pressure switch. Still did not work. Any help would be appreciated..

Check the fuse at control board. If you have one and sometimes new board does not come with fuse.
They uses blade type automotive fuse. Most of them use 3 amp fuse.

If your unit have fuse or does not require fuse then check the main reason for burnt control panel. Control panel don't burn itself, something must've cause them to burn out.