I have a ground running from the electrical panel to the cold water pipe just before the meter. The ground wire does not jump the meter & my house has failed inspection.

My questions are:
Can I splice the existing wire with an additional piece to reach past the meter or do I have to replace the entire wire to reach past the meter?
If so, is there a special connector that needs to be used to connect the wires?

Re: Grounding to water meter
therealdusk wrote:

I have a ground running from the electrical panel to the cold water pipe just before the meter. The ground wire does not jump the meter & my house has failed inspection.

My questions are:
Can I splice the existing wire with an additional piece to reach past the meter or do I have to replace the entire wire to reach past the meter?
If so, is there a special connector that needs to be used to connect the wires?

There are special connectors and methods to extend the GEG (grounding electrode conductor) but they require a special crimper or mold to make them "irreverseable". So, if it's not too long a run from the electrical panel to the cold water pipe it may be easier to just run new #4 bare copper (#6 is OK if "not subject to physical damage).

Be sure to use a waterpipe connector on the CW line within 5' of where it enters the house.

adamharington
Re: Grounding to water meter

I think instead of paying excess money in buying connectors and other things you should replace complete wire.

Mastercarpentry
Re: Grounding to water meter

Where I am, grounding to water lines is a no-go; the preferred method being dual ground rods outside as near to the meter as is practical. You'd already have the needed wire and those connectors are relatively cheap. Most electricians drive 'em in with a rotary hammer. Someone set up for this would be done in under 30 minutes and time is money! Check with the local inspector, but perhaps you can run a separate jumper from pipe to pipe across the meter, thus grounding your side of the system.

Phil

HoustonRemodeler
Re: Grounding to water meter

we can't ground to the water line either

JLMCDANIEL
Re: Grounding to water meter

While metal water lines should be grounded, the proper way to ground the service is with prperly installed ground rods. The advent and use of PEX has made the water lines an unreliable ground source.

Jack

dj1
Re: Grounding to water meter

Another vote not to use the CW pipe, even if your local code allows it.

Re: Grounding to water meter

Per 2014 NEC Art. 250.52
Any of the following electrodes which are present in a structure must be bonded together to form a grounding electrode system:
Metal underground water pipe (if at least 10 ft are buried outside) in addition, at least one other of the methods listed below must be used/installed
Metal frame
Concrete encased electrode
Ground ring
Ground rods (if present 2 are generally required)
Plate electrodes
Other local underground systems or metal structures
Except: Aluminum electrodes or metal underground gas piping