D/W and Disposal on same 15A C/B

Installing a new D/W at wife's house, noticed 15A c/b marked general lighting to be on same circuit as D/W & Disposal. It appears to control light over sink and disposal switch. I don't think the house was build w disposal b/c box that it plugs into is attached to face of cabinet and has wire coming out of bottom of box to D/W. I think this box is tied to the outside electrical box on outside opposite wall.

dj1
Re: D/W and Disposal on same 15A C/B

I prefer the dishwasher and the garbage disposer to be on separate 20 amp circuits.

dcalabro
Re: D/W and Disposal on same 15A C/B

I'm not an electrical expert but I have followed similar posts and having seen the load calculations from other experts I am convinced that your best bet is to at minimum have a dedicated 20A line to share between the garbage disposal/dishwasher.

If I were in your position, I would install a new dedicated 20A breaker for the dishwasher to use. Should be fairly cheap as well especially for the peace of mind knowing its done right.

HoustonRemodeler
Re: D/W and Disposal on same 15A C/B

In any new construction we share a 20a between the DW and GD. In remodels often times its easier to run a new line to the DW.

Brad
Re: D/W and Disposal on same 15A C/B
HoustonRemodeler wrote:

In any new construction we share a 20a between the DW and GD. In remodels often times its easier to run a new line to the DW.

Ditto.....